Question 99Electricity & Electronics - 1st Asst/Chief
70% to passA turbo generator has a rated output of 1200 kW at 60 Hertz, with a no load frequency of 61.5 Hertz. What is its speed droop?
A1.025%
B1.500%
C2.439%
D2.500%
AI Explanation
The correct answer is C) 2.439%. To calculate the speed droop, we use the formula: Speed Droop (%) = (No Load Frequency - Rated Frequency) / Rated Frequency x 100 In this case, the no load frequency is 61.5 Hz and the rated frequency is 60 Hz. Plugging these values into the formula, we get: Speed Droop (%) = (61.5 - 60) / 60 x 100 = 2.439% The other options are incorrect because: A) 1.025% is too low B) 1.500% is too low D) 2.500% is slightly higher than the correct value of 2.439%
Related Questions
Q@q.QuestionNumber:Upon loss of field excitation of a generator operating in parallel with others, ... Q@q.QuestionNumber:When replacing a fuse with one of a ampere higher rating than the original, whic... Q@q.QuestionNumber:In figure "A" of the illustration, the battery Vbb and resistor Rb are in the ci... Q@q.QuestionNumber:In process control terminology, continuously variable values which change withou... Q@q.QuestionNumber:What are some common basic applications for the operational amplifier?