70% to passWhen paralleling two AC generators, the synchroscope selector switch and frequency meter switch should be set up to sense the frequency of which of the following?
Abus transfer relay
Boncoming generator
Cbus
Dgenerator on the line
AI Explanation
The correct answer is B) oncoming generator. When paralleling two AC generators, the synchroscope selector switch and frequency meter switch should be set up to sense the frequency of the oncoming generator. This allows the operator to match the frequency of the oncoming generator to the frequency of the bus or the generator already on the line, which is a critical step in the paralleling process. The other options are incorrect because the bus transfer relay is not involved in the paralleling process, and the bus or the generator already on the line do not need to be sensed, as the oncoming generator must match their frequency.
Related Questions
Q@q.QuestionNumber:For what purpose are time delayed or delayed action-type fuses used? Q@q.QuestionNumber:To limit the current flow through a DC voltmeter to as low a value as possible, ... Q@q.QuestionNumber:With what device is the RPM of an AC generator indirectly measured on a switchbo... Q@q.QuestionNumber:A triac thyristor functions as a control device and can be thought of to functio... Q@q.QuestionNumber:What is the primary functional purpose of the KM1 contactor as shown in the illu...