Question 4Steam Plants - Assistant Engineer
70% to passWhen warming up a fuel oil service system, you should open the steam supply to the fuel oil heaters _______________.
Abefore you start the fuel oil service pump
Bbefore you open the recirculating valve
Cafter you start the fuel oil service pump
Donly if the settlers are incapable of heating the oil
AI Explanation
The correct answer is C) after you start the fuel oil service pump. When warming up a fuel oil service system, it is important to first start the fuel oil service pump to circulate the fuel oil through the system. This ensures that the fuel oil is being heated evenly throughout the system. Only after the pump is running should you open the steam supply to the fuel oil heaters. This allows the heated fuel oil to circulate and reach the appropriate temperature before the heaters are engaged. Opening the steam supply before starting the pump could result in uneven heating and damage to the system.
Related Questions
Q28:The boiler main feed stop-check valve is located nearest the _______________. Q61:In what section of a boiler would you find a steam quality of 90%? Q312:Excessive accumulation of carbon deposits on a boiler burner throat ring and di... Q356:In a regenerative air heater, air is bypassed around the heater while __________... Q91:When raising steam on a cold boiler under normal conditions, you should always _...