Coast Guard Exams
Question 768Deck Safety70% to pass

Which of the following statements is true concerning the control activators, i.e., pull-handles, push-buttons or levers, for a space protected by a CO2 fixed fire extinguishing system?

AI Explanation
The correct answer is D) All of the above. This is because the regulations for CO2 fire extinguishing systems require the following: 1) An alarm must sound for at least 20 seconds before CO2 is released into a space that is likely to be occupied, to allow time for evacuation (option A). 2) Two control activators are required when a stop valve is installed in the main discharge line to a space, to prevent accidental discharge (option C). 3) For discharge piping systems designed without a stop valve, only one control activator is required (option B). Therefore, all three statements are true regarding the control activators for a space protected by a CO2 fixed fire extinguishing system.

Ready to test your knowledge?