Question 270Electricity/Electronics - Assistant Engineer70% to pass
When a megohmmeter is used to test insulation, what condition causes the gradual rise of the pointer reading as a result of continued cranking?
AI Explanation
The correct answer is B) the dielectric-absorption effect of the insulation.
When a megohmmeter is used to test insulation, the gradual rise of the pointer reading as a result of continued cranking is caused by the dielectric-absorption effect of the insulation. This effect occurs because the insulation material has a property called dielectric absorption, which causes it to slowly absorb and store electrical energy over time when subjected to an applied voltage. As the megohmmeter continues to crank, the insulation gradually charges up, resulting in the gradual rise of the pointer reading.
The other options are incorrect because: A) leakage of current along the surface of dirty insulation would result in a decreasing pointer reading, not a gradual rise; C) good conductor resistance would not cause a gradual rise in the pointer reading; and D) the inductive reactance of the windings is not relevant to the insulation testing using a megohmmeter.
Related Questions
#268 Emergency generators are required to automatically start upon a loss of normal supply voltage, according to 46 CFR, Subchapter J (Electrical Engineering). In conducting a test of the emergency generator automatic transfer of load function, if the normal system supply voltage is 480 VAC, to what value would the normal source output voltage have to rise to trigger the automatic transfer of emergency loads back to the normal power source? #269 As shown in figure "A" of the illustration, what phenomenon is illustrated with respect to electrical cables and ground? Illustration EL-0126 #271 Which of the listed pairs of materials make the best insulators? #272 When a fluorescent lamp has reached the end of its useful life, it should be replaced immediately. If not, what condition could the resultant flashing cause? #273 What device can be used to check the calibration of a circuit breaker?