Question 310Electricity/Electronics - Assistant Engineer70% to pass
Suppose it is desired to connect a dual voltage three phase squirrel-cage induction motor for low volts, but it is undetermined whether the nine-lead motor is internally configured for wye or delta configuration. Using an ohmmeter, the motor itself with leads disconnected, and the illustration as a guide, what statement is true? Illustration EL-0134

AI Explanation
The correct answer is C.
If leads "7", "8", and "9" have continuity across each other, the motor is "wye" configured. Without continuity, the motor is "delta" configured.
This is because in a wye-connected three-phase motor, the three windings are connected in a wye configuration, and the neutral point (center of the wye) is connected to leads "7", "8", and "9". Therefore, if these leads show continuity, it indicates a wye configuration. Conversely, in a delta-connected motor, the windings are connected in a closed loop, and there is no neutral point, so the leads "7", "8", and "9" would not show continuity.
The other options are incorrect because they involve checking the wrong set of leads to determine the configuration.
Related Questions
#308 When using the test set-up shown in figure "A" of the illustration, besides the motor windings and the motor feeder cable, what circuit components are actually being meggered? Illustration EL-0027 #309 When you are making a high potential test (megger) on the motor coils of repaired electrical machinery to ground. What would a low resistance reading indicate? #311 Which of the conditions listed will indicate the need to clean the insulation on the windings of an electric motor? #312 As shown in figure "A" of the ungrounded distribution system with possible ground faults shown in the illustration, under what conditions would an outage likely occur due to a ground fault causing a circuit breaker to trip? Illustration EL-0129 #313 From the information given in the illustration, what would be the ampere capacity at full load of each of the main ship service diesel-generators if operating at the rated power factor of 0.8? Illustration EL-0106