Question 168Refrigeration/AC - Assistant Engineer70% to pass
You are checking the supply chilled water temperature thermistor probe on a high- pressure hermetic centrifugal chiller. Using the illustrated chart, what statement is true if the supply water temperature is verified 45°F with a digital thermometer? Illustration GS-RA-48
AI Explanation
The correct answer is D) When checked with control power on and the thermistor probe connected into the circuit, the thermistor probe voltage drop should be 3.805 volts.
This is correct because the illustrated chart (GS-RA-48) indicates that at a supply water temperature of 45°F, the thermistor probe voltage drop should be 3.805 volts when the control power is on and the probe is connected into the circuit.
The other options are incorrect because option A assumes the control power is off, and options B and C do not match the voltage drop value indicated on the chart for a 45°F supply water temperature.
Related Questions
#166 The pressure in the part of a high-pressure refrigeration system about to be opened for a non-major repair should be brought to what value? #167 What is the maximum volume to which refillable refrigeration cylinders should be filled? #169 A box solenoid valve used in a refrigeration system should be installed in what manner? #170 The FIRST thing to do to ensure that a refrigeration unit will not start while undergoing repairs is to do what? #171 Which of the precautions listed should be taken before opening any part of a refrigeration system for the purpose of accomplishing non-major repairs?