Question 185Refrigeration/AC - Assistant Engineer70% to pass
Concerning the proper installation of the sensing bulb of a thermal expansion valve that is attached to the evaporator tail coil on a horizontal run, what statement is true?
AI Explanation
The correct answer is D: The bulb should be attached so that the pinched off tubing should be oriented down and the capillary tube running to the valve diaphragm should be oriented up.
This is the correct answer because the orientation of the sensing bulb is important to ensure proper operation of the thermal expansion valve. With the pinched off tubing oriented downward and the capillary tube oriented upward, the bulb will be able to accurately sense the temperature of the refrigerant exiting the evaporator coil, allowing the valve to properly regulate the flow of refrigerant into the evaporator.
The other options are incorrect because they do not provide the optimal orientation for the sensing bulb to accurately measure the temperature and provide proper control of the refrigerant flow.
Related Questions
#183 Besides the evaporator pressure, the thermal expansion valve reacts directly to changes in what parameter? #184 Constant superheat is maintained at the evaporator coil outlet of a refrigeration system or unit by the action of what device? #186 In the multi-evaporator refrigeration system shown in the illustration, what is the proper name for the valve labeled "29"? Illustration GS-RA-12 #187 In refrigeration systems with multiple evaporators, the metering of refrigerant to each refrigerated space evaporator is accomplished by what device? #188 An air-cooled refrigerated container unit using R-134a as a refrigerant has a box temperature set point of -15°F, but it is currently operating with a stable return air temperature of 0°F. The fresh air makeup vent is closed, the unit is operating at 460 VAC/60 Hz, and the unit is in full capacity cool (modulating valve 100% open). Using the illustrated troubleshooting guide, what would be the normal range of expected discharge pressures if the ambient air temperature is 90°F? Illustration GS-RA-52