The rupture disc on a low-pressure centrifugal refrigeration unit is used as an overpressure protection device and is set to relieve at 15 psig and is most likely to lift when the compressor is idle. Where is the rupture disc located?
AI Explanation
The correct answer is D) on top of the chiller evaporator shell.
The rupture disc is located on the evaporator shell because it is the most likely point of overpressure in a low-pressure centrifugal refrigeration system. When the compressor is idle, the refrigerant can continue to vaporize in the evaporator, causing the pressure to rise. The rupture disc is placed on the evaporator shell to protect it from this over-pressurization.
The other options are incorrect because the condenser (A), compressor discharge (B), and economizer (C) are not the most likely points of overpressure when the compressor is not running.
Related Questions
#3 When the relief valve opens on a refrigeration compressor discharge line, it discharges high-pressure refrigerant vapor to what location? #4 Which of the lettered components shown in the illustration indicates the high-pressure cutout? Illustration GS-RA-12 #6 During the initial cooling down of a box temperature in a refrigeration system, which of the devices listed is used to prevent excessive gas pressure at the compressor suction for the purpose of prevention of overloading of the compressor driver? #7 A reheater in an air conditioning system performs what function? #8 What is one benefit of maintenance of proper air circulation in an air conditioned cargo space?