Question 165Refrigeration/AC - 1st Asst/Chief70% to pass
If a refrigeration compressor had developed a slightly high suction pressure accompanied with an abnormally low suction temperature, the problem could be a result of which of the following?
AI Explanation
The correct answer is B) liquid refrigerant flooding back from the cooling coil.
If the refrigeration compressor has a slightly high suction pressure accompanied by an abnormally low suction temperature, it indicates that there is an issue with the refrigerant flow, specifically liquid refrigerant flooding back from the cooling coil. This can happen when the cooling load is too high or the refrigerant flow is restricted, leading to an excess of liquid refrigerant in the suction line, which can be drawn into the compressor and cause the observed symptoms.
The other options are incorrect because: A) a clogged sub cooler would likely result in high suction pressure and high suction temperature, not low; C) a minor accumulation of air or non-condensable gases would cause high suction pressure and high suction temperature; and D) a leaking king valve would not directly cause the observed symptoms.
Related Questions
#163 Why can CFC or HCFC refrigerants leaking into a confined space or in limited surroundings cause suffocation? #164 While troubleshooting intermittent failures of the ship service refrigeration system you suspect the problem is with the lube oil pressure differential switch. The recommended course of action would be: #166 If a refrigeration system, equipped with a reciprocating compressor, has a liquid-line solenoid valve that is leaking during the 'off' cycle, what would this cause? #167 Moisture in a refrigeration system can cause which of the following conditions? #168 During tests to discover why a refrigeration compressor is running continuously, it is determined that the refrigerated space temperature is slightly above normal without ever reaching the desired minimum temperature. Suction and discharge pressures are normal for the corresponding box temperature. In this situation, what should you suspect?