Question 88Refrigeration/AC - 1st Asst/Chief70% to pass
If increasing the cooling water flow to a refrigeration condenser fails to lower the condenser pressure, the probable cause may be due to what condition?
AI Explanation
The correct answer is B) excessive amount of non-condensable gases trapped in the condenser.
When non-condensable gases (such as air) are present in the refrigeration system, they will accumulate in the condenser, reducing the effective surface area for heat transfer. This results in higher condenser pressure, even if the cooling water flow is increased. The other options are incorrect because they would not directly cause a higher condenser pressure if the cooling water flow is increased. A partially blocked thermal expansion valve (A) would affect the evaporator performance, not the condenser. An evaporator coil in need of defrosting (C) would not impact the condenser pressure. A low level of refrigerant (D) could reduce cooling capacity, but would not necessarily increase condenser pressure if the cooling water flow is adequate.
Related Questions
#86 Low compressor head pressure in a refrigeration system can be caused by which of the following? #87 High suction pressure accompanied by low suction temperature to a refrigeration system compressor is caused by which of the following? #89 In an operating, water-cooled, multi-box refrigeration system, both low discharge and high suction pressures are being simultaneously experienced. The probable cause for this condition is which of the following? #90 Which of the listed statements describes the reason why oil foaming occurs when starting a refrigeration compressor? #91 In a refrigeration plant, what is one vital purpose of the receiver?