You are checking the supply chilled water temperature thermistor probe on a high- pressure hermetic centrifugal chiller. Using the illustrated chart, what statement is true if the supply water temperature is verified 45°F with a digital thermometer? Illustration GS-RA-48
AI Explanation
The correct answer is C) When checked with control power on and the thermistor probe connected into the circuit, the thermistor probe voltage drop should be 3.805 volts.
This is correct because at a supply water temperature of 45°F, the thermistor probe's resistance will result in a voltage drop of 3.805 volts when the probe is connected into the circuit with control power on. The thermistor probe's resistance changes with temperature, and the chart provided illustrates the expected voltage drop at different temperatures.
The other options are incorrect because option A assumes the probe is isolated, option B gives an incorrect voltage drop, and option D assumes the power is off, which would not provide the necessary voltage to measure the thermistor probe's resistance.
Related Questions
#79 If a refrigeration system compressor crankcase is exhibiting an unusual degree of sweating or frosting and is operating noisily, what should be done? #80 If increasing the cooling water flow to a refrigeration condenser fails to lower the condenser pressure, the probable cause may be due to what condition? #82 Refrigeration systems using forced air circulation evaporators have a tendency to cause rapid dehydration of produce in chill boxes. Which of the following will minimize this dehydration? #83 A box solenoid valve used in a refrigeration system should be installed in what manner? #84 The thermostat controlling the operation of the solenoid valve to a refrigerated box evaporator senses what temperature?