Question 506Electricity/Electronics - Assistant Engineer70% to pass
Upon loss of field excitation of a generator operating in parallel with others, what must be done?
AI Explanation
The correct answer is A) The parallel-connected generator which has suffered the loss of field excitation must be immediately disconnected from the bus by tripping its circuit breaker.
When a generator loses its field excitation while operating in parallel with other generators, it will start to draw leading reactive power from the bus, which can lead to system instability and potential damage to the generator. The immediate solution is to disconnect the affected generator from the bus to prevent it from destabilizing the power system. The other options are incorrect because over-exciting the remaining generators, stopping the prime mover, or reducing it to idle speed will not address the root issue of the loss of field excitation in the affected generator.
Related Questions
#504 Under unusual circumstances, it may be required to operate a ship's service generator above its rated kVA. What supplemental casualty control action will be required? #505 As shown in the illustrated one-line diagram of a two-tiered emergency power system for a passenger ship, what statement is true? Illustration EL-0166 #507 If it becomes absolutely necessary to run an alternator at lower than 5% below its rated frequency, in terms of output voltage, what must be done? #508 In the illustrated one-line diagram, if the ship's service generator on line fails, what statement is true concerning the operation of the emergency diesel-generator? Illustration EL-0014 #509 For a motor rated at 3.3 kV, what would be a minimum accepted insulation resistance to hull ground as tested by an appropriate megger (insulation tester)?