If a refrigeration compressor were short cycling on the low pressure cutout switch, what is the most probable cause?
AI Explanation
The correct answer is C) the expansion valve strainers were fouled.
If a refrigeration compressor is short cycling on the low pressure cutout switch, the most probable cause is that the expansion valve strainers are fouled. This restricts the flow of refrigerant through the expansion valve, leading to a sudden drop in suction pressure and triggering the low pressure cutout switch.
The other options are incorrect because: A) the high pressure switch adjustment would not affect the low pressure side, B) an overcharge would typically lead to high pressure issues, not low pressure, and D) slight suction valve leakage would not cause such dramatic pressure drops.
Related Questions
#79 A refrigeration unit will tend to short-cycle when operating under what conditions? #80 A reciprocating multi-cylinder air conditioning or refrigeration compressor starts cycling on/off. What would one do to prevent cycling? #82 When starting a reciprocating refrigeration compressor that has been shut down for a period of time, you should manually throttle which valve? #83 What is the purpose of running a refrigeration compressor in short intermittent spurts or throttling the suction isolation valve when starting the system after a prolonged shutdown? #84 An air-cooled refrigerated container unit using R-134a as a refrigerant has a box temperature set point of -15°F, but it is currently operating with a stable return air temperature of 0°F. The fresh air makeup vent is closed, the unit is operating at 460 VAC/60 Hz, and the unit is in full capacity cool (modulating valve 100% open). Using the illustrated troubleshooting guide, what would be the normal range of expected discharge pressures if the ambient air temperature is 90°F? Illustration GS-RA-52