Question 83Refrigeration/AC - 1st Asst/Chief70% to pass
What is the purpose of running a refrigeration compressor in short intermittent spurts or throttling the suction isolation valve when starting the system after a prolonged shutdown?
AI Explanation
The correct answer is B) prevent liquid slugging or overloading the compressor.
When starting a refrigeration system after a prolonged shutdown, the compressor should not be run continuously at full capacity. Doing so could lead to liquid refrigerant entering the compressor, known as "liquid slugging," which can damage the compressor. Instead, the compressor should be operated in short, intermittent spurts or the suction isolation valve should be throttled to gradually cool the refrigerated compartment. This allows the refrigerant to properly evaporate and prevents the compressor from being overloaded, protecting the system from potential damage.
The other options are incorrect because A) is not necessary, C) is an incomplete explanation, and D) is unrelated to the purpose of the starting procedure.
Related Questions
#81 If a refrigeration compressor were short cycling on the low pressure cutout switch, what is the most probable cause? #82 When starting a reciprocating refrigeration compressor that has been shut down for a period of time, you should manually throttle which valve? #84 An air-cooled refrigerated container unit using R-134a as a refrigerant has a box temperature set point of -15°F, but it is currently operating with a stable return air temperature of 0°F. The fresh air makeup vent is closed, the unit is operating at 460 VAC/60 Hz, and the unit is in full capacity cool (modulating valve 100% open). Using the illustrated troubleshooting guide, what would be the normal range of expected discharge pressures if the ambient air temperature is 90°F? Illustration GS-RA-52 #85 If the running suction pressure at the refrigeration compressor of a TXV controlled air- cooled refrigeration system is below normal, which of the following can be a cause? #86 Low compressor head pressure in a refrigeration system can be caused by which of the following?