Question 253Electricity/Electronics - Assistant Engineer70% to pass
If the motor shown in the illustration will not start when the "off-run" switch is placed in the run position, which of the listed components should be checked FIRST? Illustration EL-0017

AI Explanation
The correct answer is B) check the overload relay for tripped condition, reset as necessary.
The reasoning behind this is that if the motor will not start when the "off-run" switch is placed in the run position, the most likely cause is that the overload relay has tripped, which is designed to protect the motor from overloading. Checking the overload relay for a tripped condition and resetting it as necessary would be the first step in troubleshooting the issue.
The other answer choices are not correct because: A) checking the main contactor coil is not the first step, C) checking the overload relay heaters is unnecessary if the relay has simply tripped, and D) checking the disconnect switch is not relevant if the switch is already in the run position.
Related Questions
#251 The turns ratio of the tapped step-down transformer shown in figure "C" of the illustration is four to one and all taps are evenly spaced. If 120 volts were applied to terminals 'H1' and 'H3', what would appear at 'X1' and 'X2'? Illustration EL-0082 #252 In figure "4" of the diagram in the illustration, the three phase step-down power transformer has a turns ratio of five to one. If a three-phase 4160 volt supply is connected to terminals "A1-B1-B2", what voltage should develop across terminals "A2- B2-C2"? Illustration EL-0084 #254 The motor fails to start on an attempted startup. With the start button depressed, a voltmeter reading between 1 and 5, as in figure "A" shown in the illustration, indicates line voltage available to the control circuit, what should be your next step in the troubleshooting process? Illustration EL-0007 #255 In order to properly set up programmable motor protection, it is necessary to know the locked-rotor current of a motor. Given the chart of code letters for locked-rotor kVA/HP and the necessary instructions shown in the illustration, calculate the estimated locked-rotor current for the motor represented by the illustrated motor nameplate using a mid-range value for the code letter, assuming the motor is to run at 440 VAC. Illustration EL-0175 #256 As shown in figure "B" of the typical ground fault relay shown in the illustration, what statement concerning the leakage current setting adjustment is true? Illustration EL-0223