Question 254Electricity/Electronics - Assistant Engineer70% to pass
The motor fails to start on an attempted startup. With the start button depressed, a voltmeter reading between 1 and 5, as in figure "A" shown in the illustration, indicates line voltage available to the control circuit, what should be your next step in the troubleshooting process? Illustration EL-0007

AI Explanation
The correct answer is A) attempt to reset the overload relay and determine the cause of the overload if applicable.
The reasoning is that with a voltmeter reading between 1 and 5 volts, indicating line voltage available to the control circuit, the issue is likely related to an overload condition that has tripped the overload relay, preventing the motor from starting. The next logical step would be to reset the overload relay and investigate the cause of the overload, which could be due to a variety of factors such as a mechanical issue, a faulty component, or an overloaded circuit.
The other options are not the correct next step in the troubleshooting process. Testing the stop button for continuity (B) or ensuring the disconnect switch is closed (C) would not address the specific issue indicated by the voltmeter reading. Testing the contactor coil "M" for continuity (D) may be a subsequent step, but it is not the immediate next step in the troubleshooting process.
Related Questions
#252 In figure "4" of the diagram in the illustration, the three phase step-down power transformer has a turns ratio of five to one. If a three-phase 4160 volt supply is connected to terminals "A1-B1-B2", what voltage should develop across terminals "A2- B2-C2"? Illustration EL-0084 #253 If the motor shown in the illustration will not start when the "off-run" switch is placed in the run position, which of the listed components should be checked FIRST? Illustration EL-0017 #255 In order to properly set up programmable motor protection, it is necessary to know the locked-rotor current of a motor. Given the chart of code letters for locked-rotor kVA/HP and the necessary instructions shown in the illustration, calculate the estimated locked-rotor current for the motor represented by the illustrated motor nameplate using a mid-range value for the code letter, assuming the motor is to run at 440 VAC. Illustration EL-0175 #256 As shown in figure "B" of the typical ground fault relay shown in the illustration, what statement concerning the leakage current setting adjustment is true? Illustration EL-0223 #257 What can be the cause of excessive heat or burning contacts in an operating motor controller?